CFL - Compact Fluoros (varcne zarnice)
Sam's F-Lamp FAQ
Fluorescent Lamps, Ballasts, and Fixtures
Principles of Operation, Circuits, Troubleshooting, Repair
Version 1.90
Copyright (C) 1994,1995,1996,1997,1999
Samuel M. Goldwasser
--- All Rights Reserved ---
Corrections or suggestions to:
sam@stdavids.marconimed.com
Reproduction of this document in whole or in part is permitted if both of the following conditions are satisfied:
This notice is included in its entirety at the beginning.
There is no charge except to cover the costs of copying.
Table of Contents
Preface
Author & Copyright
DISCLAIMER
Acknowledgements
Introduction
Fluorescent Lamp Basics
Fluorescent Lamp Labeling
Safely Working with Fluorescent Lamps and Fixtures
Fluorescent Fixtures and Ballasts
Fluorescent Fixtures
Fluorescent Lamp Ballasts
Types of Iron Ballasts
Electronic Ballasts
Fluorescent fixture wiring diagrams
Wiring for Preheat Fluorescent Fixtures
Fluorescent Starter Operation
Wiring for Rapid Start and Trigger Start Fixtures
Wiring Diagram for Single Tube Rapid or Trigger Start Ballast
Wiring Diagram for Two Tube Rapid Start Ballast
Schematic of Typical Rapid/Trigger Start Single Lamp Ballast
Schematic for Rapid Start Ballast with Isolated Secondary
Schematic of Rapid Start Dual Lamp Ballast
Measurements of Dual Tube Rapid Start Ballasts
Fluorescent Lamps in Series?
Fluorescent Lamps in Parallel?
Wiring Fluorescent Lamps to Remote Ballasts
Wiring diagram of Low Power 220 VAC Fluorescent Lamp
Specialty Fluorescent Lamp Types
All Sorts of Less Conventional Lamps
Blacklight Fluorescent Lamps
Compact Fluorescent Lamps
Cold Weather Fluorescent Lamps
Troubleshooting of Fluorescent Lamps and Fixtures
Problems with Fluorescent Lamps and Fixtures
Comments on Black Bands and Other Fluorescent Failure Issues
Why is a Grounded Fixture Needed for Reliable Starting?
Why Do Fluorescent Lamps Buzz and What to Do About It?
Why Fluorescent Lamps are Sometimes Dimmer than Expected
Rings or Swirls of Light in Fluorescent Lamps
Comments on Instant Start/Rapid Start Compatibility
Premature Cathode Failure in Dimmed Fluorescent Lamps
Items of Interest
All Those Different Wattage 4-Foot and F40 and "Shop Light" Lamps?
What's with All Those Different Shades of White?
Why Small Fluorescent lamps Cost More than 4-Foot Ones
Energy Consumption and Wear-And-Tear due to Starting
What Happens when Fluorescent Lamps Wear Out
Blackening at Ends of Fluorescent Tubes
Hot Cathode Versus Cold Cathode Operation
Comments on Small Inverter Powered Fluorescent Lamps
Operating a Fluorescent Lamp on DC
Ballasts and PCBs (The Hazmat Type)
Driving Cold Cathode Fluorescent Lamps
What is the E-Lamp?
Back to Sam's F-Lamp FAQ Table of Contents.
Preface
Author and Copyright
Author: Samuel M. Goldwasser
Corrections/suggestions:
sam@stdavids.marconimed.com
Copyright (c) 1994,1995,1996,1997,1998,1999
All Rights Reserved
Reproduction of this document in whole or in part is permitted if both of the following conditions are satisfied:
1.This notice is included in its entirety at the beginning.
2.There is no charge except to cover the costs of copying.
DISCLAIMER
We will not be responsible for damage to equipment, your ego, county wide power outages, spontaneously generated mini (or larger) black holes, planetary disruptions, or personal injury or worse that may result from the use of this material.
Acknowledgements
Thanks to Don Klipstein (don@misty.com) for his comments and additions to this document. His Web site (http://www.misty.com/~don/) is a valuable resource for information relating to lighting technology in general and also includes additional articles dealing with fluorescent and other discharge lamps.
Back to Flamp FAQ Table of Contents.
Introduction
Fluorescent Lamp Basics
The fluorescent lamp was the first major advance to be a commercial success in small scale lighting since the tungsten incandescent bulb. Its greatly increased efficiency resulted in cool (temperature wise) brightly lit workplaces (offices and factories) as well as home kitchens and baths. The development of the mercury vapor high intensity discharge (HID) lamp actually predates the fluorescent (the latter being introduced commercially in 1938, four years after the HID). However, HID type lamps have only relatively recently become popular in small sizes for task lighting in the home and office; yard and security area lighting; and light source applications in overhead, computer, and video projectors.
Fluorescent lamps are a type of gas discharge tube similar to neon signs and mercury or sodium vapor street or yard lights. A pair of electrodes, one at each end - are sealed along with a drop of mercury and some inert gases (usually argon) at very low pressure inside a glass tube. The inside of the tube is coated with a phosphor which produces visible light when excited with ultra-violet (UV) radiation. The electrodes are in the form of filaments which for preheat and rapid or warm start fixtures are heated during the starting process to decrease the voltage requirements and remain hot during normal operation as a result of the gas discharge (bombardment by positive ions).
When the lamp is off, the mercury/gas mixture is non-conductive. When power is first applied, a high voltage (several hundred volts) is needed to initiate the discharge. However, once this takes place, a much lower voltage - usually under 100 V for tubes under 30 watts, 100 to 175 volts for 30 watts or more - is needed to maintain it.
The electric current passing through the low pressure gases emits quite a bit of UV (but not much visible light). The gas discharge's radiation is almost entirely mercury radiation, although the gas mixture is mostly inert gas and generally around something like 1 percent mercury vapor. The internal phosphor coating very efficiently converts most of the UV to visible light. The mix of the phosphor(s) is used to tailor the light spectrum to the intended application. Thus, there are cool white, warm white, colored, and black light fluorescent (long wave UV) lamps. There are also lamps intended for medical or industrial uses with a special envelope such as quartz that passes short wave UV radiation. Some have an uncoated envelope, and emit short-wave UV mercury radiation. Others have phosphors that convert shortwave UV to medium wave UV.
(Caution: Some specialty UV lamps emit shortwave or medium wave UV which is harmful and should not be used without appropriate protection or in an enclosure which prevents the escape of harmful UV radiation.)
Fluorescent lamps are about 2 to 4 times as efficient as incandescent lamps at producing light at the wavelengths that are useful to humans. Thus, they run cooler for the same effective light output. The bulbs themselves also last a lot longer - 10,000 to 20,000 hours vs. 1000 hours for a typical incandescent. However, for certain types of ballasts, this is only achieved if the fluorescent lamp is left on for long periods of time without frequent on-off cycles.
Fluorescent Lamp Labeling
The actual fluorescent tubes are identified by several letters and numbers and will look something like 'F40CW-T12' or 'FC12-T10'.
So, the typical labeling is of the form FSWWCCC-TDD (variations on this format are possible):
F - Fluorescent lamp. G means Germicidal shortwave UV lamp.
S - Style - no letter indicates normal straight tube; C for Circline.
WW - Nominal power in Watts. 4, 5, 8, 12, 15, 20, 30, 40, etc.
CCC - Color. W=White, CW=Cool white, WW=Warm white, BL/BLB=Black light, etc.
T - Tubular bulb.
DD - Diameter of tube in of eighths of an inch. T8 is 1", T12 is 1.5", etc.
For the most common T12 (1.5 inch) tube, the wattage (except for newer energy saving types) is usually 5/6 of the length in inches. Thus, an F40-T12 tube is 48 inches long.
Back to Flamp FAQ Table of Contents.
Safely Working with Fluorescent Lamps and Fixtures
There aren't many dangers associated with typical fluorescent lamps and fixtures:
Electric shock. There is usually little need to probe a live fixture. Most problems can be identified by inspection or with an ohmmeter or continuity tester when unplugged.
Fluorescent lamps and fixtures using iron ballasts are basically pretty inert when unplugged. Even if there are small capacitors inside the ballast(s) or for RFI prevention, these are not likely to bite. However, you do have to remember to unplug them before touching anything!
However, those using electronic ballasts can have some nasty charged capacitors so avoid going inside the ballast module and it won't hurt to check between its outputs with a voltmeter before touching anything. Troubleshooting the electronic ballast module is similar to that of a switchmode power supply. See the document: Notes on the Troubleshooting and Repair of Small Switchmode Power Supplies
Nasty chemicals: While the phosphors on the inside of fluorescent tubes are not particularly poisonous, there is a small amount of metallic mercury and contact with this substance should be avoided. If a tube breaks, clean up the mess and dispose of it properly and promptly. Of course, don't go out of your way to get cut on the broken glass!
And take care around sharp sheet metal!
Back to Sam's F-Lamp FAQ Table of Contents.
Fluorescent Fixtures and Ballasts
Fluorescent Fixtures
The typical fixture consists of:
Lamp holder - the most common is designed for the straight bipin base bulb. The 12, 15, 24, and 48 inch straight fixtures are common in household and office use. The 4 foot (48") type is probably the most widely used size. U shaped, circular (Circline(tm).) and other specialty tubes are also available.
Ballast(s) - these are available for either 1 or 2 lamps. Fixtures with 4 lamps usually have two ballasts. See the sections below on ballasts. The ballast performs two functions: current limiting and providing the starting kick to ionize the gas in the fluorescent tube(s).
Switch - on/off control unless connected directly to building wiring in which case there will be a switch or relay elsewhere. The power switch may have a momentary 'start' position if there is no starter and the ballast does not provide this function.
Starter (preheat fixtures only) - device to initiate the electrode preheating and high voltage "kick" needed for starting. In other fixture types, the ballast handles this function.
Fluorescent Lamp Ballasts
For a detailed explanation, check your library. Here is a brief summary.
A ballast serves two functions:
1. Provide the starting kick.
2. Limit the current to the proper value for the tube you are using.
In the old days fluorescent fixtures had a starter or a power switch with a 'start' position which is in essence a manual starter. Some cheap ones still do use this technology.
The starter is a time delay switch which when first powered, allows the filaments at each end of the tube to warm up and then interrupts this part of the circuit. The inductive kick as a result of interrupting the current through the inductive ballast provides enough voltage to ionize the gas mixture in the tube and then the current through the tube keeps the filaments hot - usually. You will notice that a few iterations are sometimes needed to get the tube to light. The starter may keep cycling indefinitely if either it or one of the tubes is faulty. While the lamp is on, a preheat ballast is just an inductor which at 60 Hz (or 50 Hz) has the appropriate impedance to limit the current to the tube(s) to the proper value.
Ballasts must generally be fairly closely matched to the lamp in terms tube wattage, length, and diameter.
Types of Iron Ballasts
Instant start, trigger start, rapid start, etc. ballasts include loosely coupled high voltage windings and other stuff and do away with the starter:
The ballast for a preheat fixture (combined with a starter or power switch with a 'start' position) is basically a series inductor. Interrupting current through the inductor provides the starting voltage.
The ballast for a rapid start fixture has in addition small windings for heating the filaments reducing the required starting voltage to 250 to 400 V. There are probably the most common types in use today. Trigger start fixtures are similar to rapid start fixtures.
The ballast for an instant start fixture has a loosely coupled high voltage transformer winding providing about 500 to 600 V for starting in addition to the series inductor. The electrodes of "instant start" bulbs are designed for starting without preheating. In fact, they are shorted out internally and are thus incompatible with preheat and rapid start ballasts (and they have only a single pin at each end!). The electrodes still emit electrons due to thermal emission but since they are shorted out cannot be pre-heated. That is why they require a higher starting voltage from the ballast. They they light instantly, but this slightly reduces lamp life.
Starting voltage is either provided by the inductive kick upon interruption of the current bypassed through the starter for (1) or a high voltage winding in (2) and (3).
In all cases, the current limiting is provided primarily by the impedance of the series inductance at 60 Hz (or 50 Hz depending on where you live).
(From: Vic Roberts (kirther@ix.netcom.com).)
The most basic ballast is nothing more than a current limiting device, such as an inductor, resistor or capacitor. For 50 and 60 Hz applications, the most common current limiting device is an inductor.
A simple current limiter works best when the line voltage is at least 2 times the lamp voltage. So, a simple inductor can be used in Europe, where the line voltage is 220 to 240 VAC, to operate a 4 foot lamp, which operates at 85 to 100 volts, depending upon design.
In the US and other places that use 120 VAC lines the ballast is a combination autotransformer (to raise the voltage) and inductor (the current limiter).
In addition, a Rapid Start ballast has additional windings to supply about 3.6 VAC to heat the filaments.
(From: Asimov (Asimov@juxta.mn.pubnix.ten).)
A ballast is a simple transformer with a very high impedance secondary winding which makes its current self-limiting. It also has windings for each lamp filaments. At startup the filaments get most of the power and heat up to facilitate ionization.
Meanwhile the secondary builds up a very high EMF which finally fully ionizes the plasma between both filaments. At this point the effective resistance of the conducting plasma is quite low and the current flow is limited by the secondary's impedance. This also partially saturates the core and as consequence reduces power to the filaments.
The usual failure in ballasts is that the secondary's insulation deteriorates and it starts leaking to ground. Often because the proper wiring polarity was not observed. The secondary can thus no longer generate the high EMF required to start the plasma conducting.
The KISS test method is to use a known good lamp. If it lights, the ballast is good too. The ballast can also be tested with the power off by checking for continuity in the filament windings and a very high resistance to ground for each filament. Don't try this with power on!
(From: Craig J. Larson (larson@freenet.msp.mn.us).)
Call Magnetek, a ballast manufacturer on 1-800-BALLAST. Ask for a copy of their Troubleshooting & Maintenance Guide for Linear Fluorescent Lighting Systems. Its a nice little guide book for teaching you the basics.
Electronic Ballasts
These devices are basically switching power supplies that eliminate the large, heavy, 'iron' ballast and replace it with an integrated high frequency inverter/switcher. Current limiting is then done by a very small inductor, which has sufficient impedance at the high frequency. Properly designed electronic ballasts should be very reliable. Whether they actual are reliable in practice depends on their location with respect to the heat produced by the lamps as well as many other factors. Since these ballasts include rectification, filtering, and operate the tubes at a high frequency, they also usually eliminate or greatly reduce the 100/120 Hz flicker associated with iron ballasted systems. However, this is not always the case and depending on design (mainly how much filtering there is on the rectified line voltage), varying amounts of 100/120 can still be present.
I have heard, however, of problems with these relating to radio frequency interference from the ballasts and tubes. Other complaints have resulted due to erratic behavior of electronic equipment using infra red remote controls.
There is a small amount of IR emission from the fluorescent tubes themselves and this ends up being pulsed at the inverter frequencies which are sometimes similar to those used by IR hand held remote controls.
Some electronic ballasts draw odd current waveforms with high peak currents. This is due to the fact that these ballasts (low-power-factor type) have a full-wave-bridge rectifier and a filter capacitor. Current can only be drawn during the brief times that the instantaneous line voltage exceeds the filter capacitor voltage.
Because of the high peak currents drawn by some electronic ballasts, it is often important to size wiring properly for these high peak currents. For wiring heating and fuse/circuit considerations, one should allow for a current of 4 to 6 times the ratio of lamp watts to line volts. For wiring voltage drop considerations (drop in voltage the ballast's filter capacitor gets charged to), the effective current is even higher, sometimes as high as 15 to 20 times the ratio of the lamp watts to RMS line volts.
For less than 50 watts, the current drawn by low-power-factor electronic ballasts is usually not a problem. For multiple ballasts or total wattages over 50 watts, it may be important to consider the effective current drawn by low-power-factor electronic ballasts.
If you want to get an idea of some typical modern electronic ballast designs, see the International Rectifier web site. Search for 'electronic ballasts' or download the following reference design notes:
Linear Ballast
Compact Ballast
Back to Sam's F-Lamp FAQ Table of Contents.
Fluorescent Fixture Wiring Diagrams
Wiring for Preheat Fluorescent Fixtures
The following is the circuit diagram for a typical preheat lamp - one that uses a starter or starting switch.
Power Switch +-----------+
Line 1 (H) o------/ ---------| Ballast |-----------+
+-----------+ |
|
.--------------------------. |
Line 2 (N) o---------|- Fluorescent -|----+
| ) Tube ( |
+---|- (bipin) -|----+
| '--------------------------' |
| |
| +-------------+ |
| | Starter | |
+----------| or starting |----------+
| switch |
+-------------+
Here is a variation that some preheat ballasts use. This type was found on a F13-T5 lamp fixture. Similar types are used for 30 and 40 watt preheat lamps. This 3-lead preheat ballast is a voltage-boosting "high leakage reactance autotransformer" used if the voltage across the tube is much over approx. 60 percent of the line voltage. For technical details on why a fluorescent lamp will not work with ordinary ballasts if the tube voltage is only slightly less than the line voltage, look at Don Klipstein's Discharge Lamp Mechanics document.
Power Switch +-------------+
Line 1 (H) o------/ --------|A Ballast |
+----------|B C|----------+
| +-------------+ |
| |
| .--------------------------. |
Line 2 (N) o-----+---|- Fluorescent -|----+
| ) Tube ( |
+---|- (bipin) -|----+
| '--------------------------' |
| |
| +-------------+ |
| | Starter | |
+----------| or starting |----------+
| switch |
+-------------+
Fluorescent Starter Operation
Starters may be either automatic or manual:
Automatic - The common type are called a 'glow tube starter' (or just starter) and contains a small gas (neon, etc.) filled tube and an optional RFI suppression capacitor in a cylindrical aluminum can with a 2 pin base. While all starters are physically interchangeable, the wattage rating of the starter should be matched to the wattage rating of the fluorescent tubes for reliable operation and long life.
The glow tube incorporates a switch which is normally open. When power is applied a glow discharge takes place which heats a bimetal contact. A second or so later, the contacts close providing current to the fluorescent filaments. Since the glow is extinguished, there is no longer any heating of the bimetal and the contacts open. The inductive kick generated at the instant of opening triggers the main discharge in the fluorescent tube. If the contacts open at a bad time - current near zero, there isn't enough inductive kick and the process repeats.
Higher-tech replacements called 'pulse starters' may be available for the simple glow tube type starter. These devices are pin compatible devices and contain a bit of electronics that detect the appropriate time to interrupt the filament circuit to generate the optimal inductive kick from the ballast. So, starting should be more reliable with few/no blink cycles even with hard-to-start lamps. They will also leave used-up tubes off, without letting them blink annoyingly.
Where a manual starting switch is used instead of an automatic starter, there will be three switch positions - OFF, ON, START:
OFF: Both switches are open.
ON: Power switch is closed.
START (momentary): Power switch remains closed and starting switch is closed.
When released from the start position, the breaking of the filament circuit results in an inductive kick as with the automatic starter which initiates the gas discharge.
Wiring for Rapid Start and Trigger Start Fixtures
Rapid start and trigger start fixtures do not have a separate starter or starting switch but use auxiliary windings on the ballast for this function.
The rapid start is now most common though you may find some labeled trigger start as well.
Trigger start ballasts seem to be used for 1 or 2 small (12-20 W) tubes. Basic operation is very similar to that of rapid start ballasts and the wiring is identical. "Trigger start" seems to refer to "rapid starting" of tubes that were designed for preheat starting.
The ballast includes separate windings for the filaments and a high voltage starting winding that is on a branch magnetic circuit that is loosely coupled to the main core and thus limits the current once the arc is struck.
A reflector grounded to the ballast (and power wiring) is often required for starting. The capacitance of the reflector aids in initial ionization of the gases. Lack of this connection may result in erratic starting or the need to touch or run your hand along the tube to start.
A complete wiring diagram is usually provided on the ballast's case.
Power is often enabled via a socket operated safety interlock (x-x) to minimize shock hazard. However, I have seen normal (straight) fixtures which lack this type of socket even where ballast labeling requires it. Circline fixtures do not need an interlock since the connectors are fully enclosed - it is not likely that there could be accidental contact with a pin while changing bulbs.
Wiring Diagram for Single Tube Rapid or Trigger Start Ballast
Below is the wiring diagram for a single lamp rapid or trigger start ballast. The color coding is fairly standard. The same ballast could be used for an F20-T12, F15-T12, F15-T8, or F14-T12 lamp. A similar ballast for a Circline fixture could be used with an FC16-T10 or lamp FC12-T10 (no interlock).
Power Switch +---------------------------+
Line 1 (H) o----/ ----------|Black Rapid/Trigger |
+------|White Start Red|------+
| +---|Blue Ballast Red|---+ |
| | +-------------+-------------+ | |
| | | | |
| | Grounded | Reflector | |
| | ----------+---------- | |
| | .-------------------------. | |
| +----|- Fluorescent -|----+ |
+------x| ) Tube ( | |
Line 2 (N) o----------------x|- (bipin or circline) -|-------+
'-------------------------'
Wiring Diagram for Two Tube Rapid Start Ballast
The following wiring diagram is for one pair (from a 4 tube fixture) of a typical rapid start 48 inch fixture. These ballasts specify the bulb type to be F40-T12 RS. There is no safety interlock on this fixture. (A similar scheme could also be used on a dual tube Circline fixture though slightly different ratings may be needed for each tube since they would be of different sizes.)
Power Switch +--------------------------+
Line 1 (H) o----/ ----------|Black Dual Tube Red|-----------+
Line 2 (N) o----------------|White Rapid Red|--------+ |
+-----|Yellow Start Blue|-----+ | |
| +--|Yellow Ballast Blue|--+ | | |
| | +-------------+------------+ | | | |
| | | | | | |
| | Grounded | Reflector | | | |
| | ----------+---------- | | | |
| | .----------------------. | | | |
| +----|- Fluorescent -|----+ | | |
| | | ) Tube 1 ( | | | |
+-------|- bipin -|-------+ | |
| | '----------------------' | |
| | .----------------------. | |
| +----|- Fluorescent -|----------+ |
| | ) Tube 2 ( | |
+-------|- bipin -|-------------+
'----------------------'
Schematic of Typical Rapid/Trigger Start Single Lamp Ballast
This ballast is marked "Trigger Start Ballast for ONE F20WT12, F15WT12, F15WT8, or F14WT12 Preheat Start Lamp. Mount tube within 1/2" of grounded metal reflector".
Voltages were measured with no bulb installed with safety interlock bypassed.
Internal wiring has been inferred from resistance and voltage measurements.
The lossy autotransformer boosts line voltage to the value needed for reliable starting with the filaments heated. It is assumed that part of the magnetic circuit is loosely coupled so that putting the lamp between Red/Red and Blue/White results in safe current limited operation once the arc has struck.
A complete fixture wiring diagram like those shown in the section: Wiring for Rapid Start and Trigger Start Fixtures will probably be provided on the label.
Numbers in () are measured DC resistances.
Red o--------------------------+
8.5 V (5) )|| Filament 1
Red o----------------------+---+ ||
| ||
+ ||
)||==|| Stepup winding/choke is
82.5 V (37) )|| || loosely coupled to main
)||==|| magnetic circuit
+ ||
| ||
+--> Black (H) o----------------------+---+ ||
| )|| Primary of starting
106.5 V (31) )|| autotransformer
115 V )||
Blue o--------------------------+ ||
| 8.5 V (3) )|| Filament 2
+--> White (N) o-----------o/o------------+ |
Interlock |
Green (G) o-----------------------------+
Schematic for Rapid Start Ballast with Isolated Secondary
As noted, rapid start fixtures do not have a separate starter or starting switch but use auxiliary windings on the ballast for this function. Here is the schematic for a typical 1-tube rapid start fixture including the internal wiring of the ballast.
This ballast includes separate windings for the filaments and a high voltage winding that is on a branch magnetic circuit that is loosely coupled and thus limits the current once the arc is struck. It is not known if this design is common. The isolated secondary and separate high voltage winding would make it more expensive to manufacture.
A complete fixture wiring diagram like those shown in the section: Wiring for Rapid Start and Trigger Start Fixtures will probably be provided on the label.
+-------+
Power Switch ||======||( |
Line 1 (H) o---/ ----+ || ||( +----+---------o to both pins
)|| ||( ( filament winding on one end
)|| ||( +--------------o
)|| ||( HV winding Grounded reflector
)|| || +=----^^^^^^^-------------------------+
)|| ||( _|_
)|| ||( +--------------o -
)|| ||( ( filament winding to both pins
Line 2 (N) o---------+ || ||( +----+---------o on other end
||======||( |
+-------+
Loose magnetic coupling in the ballast core results
in leakage inductance for current limiting.
Schematic of Rapid Start Dual Lamp Ballast
This ballast is marked "Rapid Start Ballast for TWO F40WT12 Lamps. Mount tubes within 1/2" of grounded metal reflector". This circuit was derived from the measurements listed in the section: Measurements of a Dual Tube Rapid Start Ballast.
The autotransformer boosts line voltage to the value needed for reliable starting with the filaments heated. The series capacitor of approximately 4 uF is used instead of leakage inductance to limit current to the tubes. Leakage inductance from loose magnetic coupling is used to smooth the waveform of current flowing through the tubes. The .03 uF capacitor provides a return path during starting to the yellow filament winding but is not really used during normal operation.
Numbers in () are approximate measured DC resistances.
Red 1 o--------------------------+
8.5 V (.5) )|| Tube 1 Filament 1
Red 2 o----------------------+---+ ||
_|_ ||
4 uF --- ||
| ||
+---+ ||
)||
)||
)|| HV winding
)||
)||
+---------+---+ ||
| _|_ ||
| .03 uF --- ||
| | ||
Yellow o----------------------+---+ ||
8.5 V | (.5) )|| Tubes 1 and 2 filament 2
Yellow o--------------------------+ ||
| ||
| ||
Blue 1 o------------+-------------+ ||
8.5 V (.5) )|| Tube 2 filament 1
Blue 2 o--+-----------------------+ ||
| ||
+--> Black (H) o--+-----------------------+ ||
| )|| Primary of
115 V (13) )|| autotransformer
| )||
+--> White (N) o------------o/o-----------+ ||
Interlock ||
|
Green (G) o-----------------------------+
Measurements of Dual Tube Rapid Start Ballasts
One is a Universal, the other is a Valmont.
(Measurements made with Radio Shack multimeter)
Resistance:
Measurement Universal Valmont
------------------------ ----------- -----------
White-Black 13 13
Between blues .5 .55
Between reds .5 .55
Between yellows .5 .6
Black to closer blue <.1 <.1
Blue-red open open
Blue-yellow open 5 M
Red-yellow open 20 M
Capacitance:
Blue-red ~4 uF ~3.5 uF
Blue-yellow ~.03 uF
Red-yellow ~.03 uF
Primary current, (not true RMS), various secondary load conditions:
Secondary open .32 A .35 A
60W 120V incandescent bulb .75 A .63 A
Short .48 A .53 A
Heater voltage: not measured approx. 8 V, unsteady
surprisingly independent
of secondary load
Open circuit output voltage voltage (from one red wire to one blue one, highest reading of four combinations):
Red-Blue 270 V 275 V
Fluorescent Lamps in Series?
This is not possible where line voltage is 105 to 125 VAC because this is not sufficient to sustain the discharge where two lamps are in series. Special dual lamp ballasts are required.
However, where the line voltage is 220 VAC, it is possible:
(From:
andrew@cucumber.demon.co.uk (Andrew Gabriel)
Here in UK (and probably all 220 to 250V areas), this is common:
=======
L o---+-----^^^^^^^-------+ +-----+
| Ballast | | |
| (Inductor) +|-|+ |
| | - | |
| | | +-+
| Tube 1 | | |S| Glow Starter
| | | +-+
| | - | |
| +|-|+ |
| | | |
_|_ Power Factor | +-----+
___ Correction |
| Capacitor | +-----+
| | | |
| +|-|+ |
| | - | |
| | | +-+
| Tube 2 | | |S| Glow Starter
| | | +-+
| | - | |
| +|-|+ |
| | | |
N o---+-------------------+ +-----+
Fluorescent Lamps in Parallel?
Like most gas discharge tubes, fluorescent lamps are negative resistance devices. Therefore, it isn't possible to put more than one lamp in parallel and get them both to light - additional components are needed. The following applies mostly to magnetic ballasted fixtures. Where electronic ballasts are used, all sorts of games can be played to implement wierd configurations!
Multiple lamp fixtures in countries with 110 VAC power usually have special ballasts with separate windings for this purpose. Where 220 to 240 VAC is available, it may be possible to put multiple lamps in series with individual starters. See the section: Fluorescent Lamps in Series?.
However, there is at least one application where putting two lamps is parallel makes sense: light fixtures in hard-to-reach or safety-critical areas where redundancy is desirable. With only minor modifications at most, a conventional single lamp ballast can be connected to a pair of lamps in such a way that only one will light at any given time. (Which one actually starts could be random without additional circuitry, however.) If either lamp burns out or is removed, the other will take over. The ballast must provide enough power to the filaments for starting but once started, the lamp that is on will operate normally and there should be no degradation in performance or expected lamp life (except to the extent that the unlit lamp's filaments might be kept hot).
The following is just a suggestion - I have not confirmed if or with which model ballasts these schemes will work!
For rapid start ballasts, this could be as simple as wiring all connections to the lamps in parallel - if the ballast has enough current available to power both sets of filaments for starting. For trigger start ballasts, the filament power is not an issue so it should be even easier:
Power Switch +---------------------------+
Line 1 (H) o----/ ---------|Black Rapid/Trigger |
+-----|White Start Red|--------+
| +--|Blue Ballast Red|-----+ |
| | +--------------+------------+ | |
| | | | |
| | +---------------+ | |
| | Grounded | Reflector | | |
| | ----------+---------- | | |
| | .-------------------------. | | |
| +----|- Fluorescent -|--|--+ |
| | | ) Tube ( | | | |
+--|----|- (bipin or circline) -|--|--|--+
| | '-------------------------' | | |
| | +---------------+ | |
| | Grounded | Reflector | |
| | ----------+---------- | |
| | .-------------------------. | |
| +----|- Fluorescent -|-----+ |
| | ) Tube ( | |
Line 2 (N) o---------+-------|- (bipin or circline) -|--------+
'------------------------'
Note: The interlock normally present on most rapid/trigger start fixtures have been removed to permit one lamp to operate if other is removed.
For preheat ballasts, wiring the filaments in parallel would probably result in insufficient current to either lamp for it to start reliably. If the filaments were wired in series, one lamp would probably start, but if the filament of one lamp burned out or the lamp was removed, the fixture would cease to function kind of defeating the purpose of these gyrations!
Wiring Fluorescent Lamps to Remote Ballasts
For reasonable distances, this should work reliably and be safe provided that:
This is only attempted with iron ballasts. The fire safety and reliability of electronic ballasts that are not in close proximity to the lamps is unknown. The ballast may fail catastrophically either immediately or a short time later as the circuit may depend on a low impedance (physically short) path for stability.
In addition, there will almost certainly be substantial Radio Frequency Interference (RFI) created by the high frequency currents in the long wires. The FCC police (or your neighbors) will come and get you! This may be a problem with iron ballasts as well - but probably of less severity.
Wire of adequate rating is used. The starting voltage may exceed 1 kV. Make sure the insulation is rated for at least twice this voltage. Use 18 AWG (or heavier) gauge wire.
There is no possibility of human contact either when operating or if any connectors should accidentally come loose - dangerous line voltage and high starting voltage will be present with tubes disconnected.
Note: one application that comes up for this type of remote setup is for aquarium lighting. My recommendation would be to think twice about any homebrew wiring around water. A GFCI may not help in terms of shock hazard and/or may nuisance trip due to inductive nature of the ballast (both depend at least in part on ballast design).
Wiring diagram of Low Power 220 VAC Fluorescent Lamp
(From: Manuel Kasper (mk@mediaklemm.com).)
The circuit in Low Power 220 VAC Fluorescent Lamp is from an AC line powered 'light stick'. So there's no fancy inverter circuit inside, but a simple ballast without any nasty coils - just capacitors, resistors, and diodes. A few modifications would probably be necessary to make it operate from 110 VAC. It runs the tube brighter than a similar lamp power from a 12 V inverter. (See the section: "Automotive Light Stick Inverter" in the document: Various Schematics and Diagrams. FWIW, the brand is "Brennenstuhl".
It was damn hard to open up because everything was made out of thick plastic with no screws (no wonder; it cost $6) - but thanks to a huge saw I managed to get at the guts without destroying the tube or the circuit.
Back to Sam's F-Lamp FAQ Table of Contents.
Specialty Fluorescent Lamp Types
All Sorts of Less Conventional Lamps
In addition to the boring white ones (OK, well 'white' does come in various colors!), other interesting types of lamps include all sorts of real colors (red, green, blue, yellow), blacklight lamps, germicidal lamps in which there is no phosphor coating at all and a quartz tube to transmit short-wave UV light (e.g., EPROM erasers and PCB photoresist activation), sunlamps, plant lights and special purpose specific wavelength lamps such as reprography and copier lamps.
The basic technology is extremely flexible!
(From: Bruce Potter (s602531@aix2.uottawa.ca).)
There are also High Output and Very High Output types of lamps that have a discharge current of 0.8 A and 1.5 A instead of the standard 0.3 A. HO and VHO lamps are used when high light output is desired but are being outmoded by HID lamps like metal halide.
Blacklight Fluorescent Lamps
(From: Don Klipstein (don@misty.com).)
BL in the tube designation (e.g., F40T12BL) means "blacklight", which is a fluorescent lamp with a phosphor that emits the longest largely invisible UV wavelengths that are both efficiently and fairly cheaply possible. This phosphor seems to emit a band of UV mainly from 350 to 370 nanometers, in the UV-A range.
BLB means "blacklight-blue", which differs from "blacklight" only in that the glass tube of this lamp is darkly tinted with something with a dark violet-blue color to absorb most visible light. Most UV gets through this, along with much of the dimly visible deep-violet 404.7 nanometer line of mercury. Most of the violetish-blue 435.8 nanometer line is absorbed, but enough of this wavelength gets through to largely dominate the color of the visible light from this lamp. Longer visible light wavelengths do not significantly penetrate the BLB's very deep violet-blue glass, which is known as 'Wood's glass'. The UV is the same as that of the BL lamp, being mostly between 350 and 370 nanometers.
There is a 350BL blacklight lamp, using a different phosphor that emits a band of slightly shorter UV wavelengths in the UV-A range. The reasoning for this lamp is that it is supposedly optimized for attracting insects. These lamps are one variety of UV lamps used in electric bug killers.
There are other UV fluorescent lamps. There are at least two different UV/deep violet emitting fluorescent lamps used mainly in the graphic arts industry, emitting mainly wavelengths between 360 and 420 nanometers. Possibly one of these is also used in bug killers. I have noticed one kind of UV fluorescent lamp for bug killers with a broadish band phosphor with significant output from the 360 nanometer range (maybe also shorter) into visible wavelengths around 410 to 420 nanometers or so.
There is an even shorter UV-A lamp used for suntanning purposes. I would guess the phosphor emits mainly within the 315 to 345 nanometer range. One brand of such lamps is "Uvalux".
There is even a UV-B emitting fluorescent lamp. Its phosphor emits mostly at UV-B wavelengths (286 to 315 nanometers). It is used mainly for special medicinal purposes. Exposing skin to UV-B causes erythema, which is to some extent a burn reaction of the skin to a slightly destructive irritant. Use of UV-B largely limits this to outer layers of the skin (perhaps mainly the epidermis) and to parts of the body where skin is thinner. UV-A wavelengths just over 315 nanometers can also cause sunburn, but they are more penetrating and can affect the dermis. Please note that the deadliest varieties of skin cancer usually originate in the epidermis and are usually most easily caused by UV-B rays.
There are clear UV-emitting lamps made of a special glass that lets through the main shortwave UV (UV-C) mercury radiation at 253.7 nanometers. These lamps are marketed as germicidal lamps, and ones in standard fluorescent lamp sizes have part numbers that start with G instead of F. These lamps will work in standard fluorescent lamp fixtures.
Cold-cathode germicidal lamps are also in use; these somewhat resemble "neon" tubing.
Be warned that the shortwave UV emitted by germicidal lamps is intended to be dangerous to living cells and is hazardous, especially to the conjunctiva of eyes. Signs of injury by the UV are often delayed, often first becoming apparent several minutes after exposure and peaking out a half hour to several hours afterwards.
Please note that non-fluorescent (high pressure mercury vapor discharge) sunlamps generally emit more UV-B rays rather than the tanning-range UV-A rays. These lamps do have substantial UV-A output, but mainly at a small cluster of wavelengths around 365 nanometers. Tanning is most effectively accomplished by wavelengths in the 315-345 nanometer range. In addition, no UV suntanning is completely safe.
Compact Fluorescent Lamps
These are miniaturized fluorescent lamps that usually have premium phosphors which often come packaged with an integral ballast (either iron or electronic). They typically have a standard screw base that can be installed into nearly any table lamp or lighting fixture that accepts an incandescent lamp.
Compact fluorescents are being heavily promoted as energy savings alternatives to incandescent lamps. They also have a much longer life - 6,000 to 20,000 hours compared to 750 to 1000 hours for a standard incandescent. While these basic premises are not in dispute - all is not peaches and cream:
They are often physically larger than the incandescent bulbs they replace and simply may not fit the lamp or fixture conveniently or at all.
The funny elongated or circular shape may result in a less optimal lighting pattern.
The light is generally cooler - less yellow - than incandescents - this may be undesirable and result in less than pleasing contrast with ordinary lamps and ceiling fixtures. Newer models have been addressing this issue.
Some types (usually iron ballasts) may produce an annoying 120 Hz (or 100 Hz) flicker.
Ordinary dimmers cannot be used with compact fluorescents.
Like other fluorescents, operation at cold temperatures (under around 50-60 degrees F) may result in reduced light output. Starting may also be erratic, although most compact fluorescent lamps seem to start OK at temperatures near freezing. Many types start OK near zero degrees F. Operation in an enclosed fixture often results in full light output in cool surroundings after the lamp warms up for a few minutes, as long as the initial temperature is high enough to permit a good start. However, enclosing compact fluorescents often impairs their ability to work well at higher temperatures.
There may be an audible buzz from the ballast.
They may produce Radio Frequency Interference (RFI).
The up-front cost is substantial (unless there is a large rebate): $10 to $20 for a compact fluorescent to replace a 60 W incandescent bulb!
Due to the high up-front cost, the pay-back period may approach infinity.
While their life may be 20,000 hours, a wayward baseball will break one of these $10 to $20 bulbs as easily as a 25 cent incandescent.
Nonetheless, due to the lower energy use and cooler operation, compact fluorescents do represent a desirable alternative to incandescents. Just don't open that investment account for all your increased savings just yet!
For more information, see the separate document on Compact Fluorescent Lamps.
Cold Weather Fluorescent Lamps
(From: Bruce Potter (s602531@aix2.uottawa.ca).)
There are special lamps with heavy glass jackets and/or with krypton gas filling for cold weather/freezer applications. They work best at below room-temperatures. It really annoys me when I go to the grocery store or see outside installations with dim, flickering tubes! What a waste of electricity!
Back to Sam's F-Lamp FAQ Table of Contents.
Troubleshooting of Fluorescent Lamps and Fixtures
Problems with Fluorescent Lamps and Fixtures
In addition to the usual defective or damaged plugs, broken wires in the cord, general bad connections, fluorescent lamps and fixtures have some unique problems of their own. The following assumes a lamp or fixture with a conventional iron (non-electronic) ballast. Always try a new set of fluorescent tubes and starter (where used) before considering other possible failures. If two tubes dim or flicker in unison, this means that both are powered by the same ballast. Often this means that one tube has failed, although the other tube may also be in poor condition or approaching the end of its life. Both tubes must be replaced with known good tubes in order to rule out a defective ballast.
Bad fluorescent tubes. Unlike incandescent lamps where a visual examination of the bulb itself will often identify a broken filament, there is often no way of just looking at a fluorescent tube to determine if it is bad. It may look perfectly ok though burned out fluorescents will often have one or both ends blackened. However, a blackened end is not in itself always an indication of a bad tube. Blackened ends are a somewhat reliable means of identifying bad tubes in 34 or 40 watt rapid start fixtures. Blackened ends are not as reliable an indicator in preheat or trigger start fixtures, or for tubes of 20 watts or less.
Failure of the electrodes/filaments at one or both ends of the the fluorescent tube will usually result in either a low intensity glow or flickering behavior, or sometimes in no light at all. A broken filament in a fluorescent tube used in a preheat type fixture (with a starter) will almost always result in a totally dead lamp as there will be no power to the starter. Dim glow is rare in this case and would probably be confined to the region of the broken filament if it occurs. The best approach is to simply try replacing any suspect tubes - preferably both in a pair that are driven from a single ballast.
In fixtures where a rapid start ballast runs two tubes, both tubes will go out when one fails. Sometimes one or both tubes will glow dimly and/or flicker. If one tube glows dimly and the other is completely dead, this does not indicate which tube has failed. The brighter tube may be the good one or the bad one. The bad tube usually has noticeable blackening at one end. It may pay to replace both tubes, especially if significant labor costs are involved. Also, prolonged dim-glowing may degrade the tube that did not initially fail.
In trigger start fixtures that use one ballast to power two 20 watt tubes, sometimes both tubes will blink or intermittently dim. Replacing either tube with a known good tube may fail to fix this. The tubes may continue blinking or intermittently dimming until both are replaced with brand new tubes. This sometimes indicates borderline low line voltage ("brownout", etc.), nonideal temperatures, or a borderline (probably cheaply designed) ballast.
Bad starter (preheat fixtures only). The little starter can may go bad or be damaged by faulty fluorescent tubes continuously trying to start unsuccessfully. It is a good idea to replace the starter whenever tubes are replaced in these types of fixtures. One way that starters go bad is to "get stuck". Symptoms of this are the ends of the affected tube glowing, usually with an orange color of some sort or another but sometimes with a color closer to the tube's normal color if arcs form across the filaments. Occaisionally, only one end arcs and glows brightly, and the other end glows dimmer with a more orange color.
Please note that this is hard on both the tube and the ballast, and the defective starter should be immediately removed.
Should one or both ends glow with a bright yellowish orange color with no sign of any arc discharge surrounding each filament, then the emissive material on the filaments is probably depleted or defective. In such a case, the tube should be replaced regardless of what else is wrong. If both ends glow a dim orange color, then the filaments' emissive coating may or may not be in good shape. It takes approx. 10 volts to form an arc across a healthy fluorescent lamp filament.
Defective iron ballast. The ballast may be obviously burned and smelly, overheated, or have a loud hum or buzz. Eventually, a thermal protector built into many ballasts will open due to the overheating (though this will probably reset when it cools down). The fixture may appear to be dead. A bad ballast could conceivably damage other parts as well and blow the fluorescent tubes. If the high voltage windings of rapid start or trigger start ballasts are open or shorted, then the lamp will not start.
Ballasts for fixtures less than 30 watts usually do not have thermal protection and in rare cases catch fire if they overheat. Defective fixtures should not be left operating.
Bad sockets. These can be damaged through forceful installation or removal of a fluorescent tube. With some ballasts (instant start, for example), a switch contact in the socket prevents generation of the starting voltage if there is no tube in place. This minimizes the possibility of shock while changing tubes but can also be an additional spot for a faulty connection.
Lack of ground. For fluorescent fixtures using rapid start or instant start ballasts, it is often necessary for the metal reflector to be connected to the electrical system's safety ground. If this is not done, starting may be erratic or may require you to run your hand over the tube to get it to light. In addition, of course, it is an important safety requirement.
Warning: electronic ballasts are switching power supplies and need to be serviced by someone qualified in their repair both for personal safety as well as continued protection from electrical and fire hazards.
Comments on Black Bands and Other Fluorescent Failure Issues
(From: Don Klipstein (don@Misty.com).)
Fluorescent tubes failing in this manner normally draw reduced current. The voltage across the tube is higher and the tube will sometimes draw more power, but the current flowing through the ballast is less.
Since the ends of the bulb usually burn out unequally, some "net DC" may try to flow through the ballast. My experience is that the feared core saturation effects do not occur. Furthermore, the common rapid start ballasts have a capacitor in series with the secondary windings which would block any DC.
There is a different problem that I once knew of causing a fire: Starters getting stuck in the "closed" state. The symptom is the ends of the tube glowing brightly, either yellow-orange or a color closer to the normal tube color, sometimes even one end glowing yellow-orange and one end glowing a more normal color. Excessive ballast current flows in this case. This is not a problem with "instant start", "rapid start", or "trigger start" fixtures. It is only a problem where there are starters.
A dim orange or red-orange glow more likely indicates dead tubes on a rapid start or trigger start ballast. If the fixture is a preheat type, dim orange end glow indicates less current than a brighter yellow-orange, and the ballast is less likely to overheat. Different brands of ballasts are designed a little differently.
If a preheat fixture has the tube glowing only in the ends, it is recommended to immediately remove the tube to stop the ballast from possibly overheating. You should replace both the tube and the starter. The starter is bad if this occurs, and the tube is usually bad also. Typically, the starter goes bad after too much time trying to start a bad tube. In the unlikely event the starter had the initial failure, the tube will be damaged by prolonged excessive end glow.
Why is a Grounded Fixture Needed for Reliable Starting?
Many fluorescent fixtures will not start reliably unless they are connected to a solid earth (safety) ground. This is most likely the case with rapid or trigger start magnetic ballasts. These will usually state on the label: "Mount tube within 1/2 inch of grounded metal reflector". If this is not done or if the entire fixture is not grounded, starting will be erratic - possibly taking a long or random amount of time to start or waiting until you brush your hand along the tube.
The reason is straightforward:
The metal reflector or your hand provides a capacitive path to ground through the wall of the fluorescent tube. This helps to ionize the gases inside the tube and initiate conduction in the tube. However, once current is flowing from end-to-end, the impedance in the ballast circuit is much much lower than this capacitive path. Thus, the added capacitance is irrelevant once the tube has started.
The reason that this is required is probably partly one of cost: it is cheaper to manufacture a ballast with slightly lower starting voltage but require the fixture to be grounded - as it should be for safety anyhow.
Why Do Fluorescent Lamps Buzz and What to Do About It?
The buzzing light is probably a mundane problem with a defective or cheap ballast. There's also the possibility of sloppy mechanical construction which lets something vibrate from the magnetic field of the ballast until thermal expansion eventually stops it.
First check for loose or vibrating sheetmetal parts - the ballast may simply be vibrating these and itself not be defective.
Most newer fixtures are of the 'rapid start' or 'warm start' variety and do not have starters. The ballast has a high voltage winding which provides the starting voltage.
There will always be a ballast - it is necessary to limit the current to the tube(s) and for starting if there is no starter. In older fixtures, these will be big heavy magnetic choke/transformer devices - hard to miss if you open the thing. Cheap and/or defective ones tend to make noise. They are replaceable but you need to get one of the same type and ratings - hopefully of higher quality. A new fixture may be cheaper.
The starter if present is a small cylindrical aluminum can, approximately 3/4" x 1-1/2" in a socket, usually accessible without disassembly. It twists counterclockwise to remove. They are inexpensive but probably not your problem. To verify, simply remove the starter after the lamp is on - it is not needed then.
The newest fixtures may use totally electronic ballasts which are less likely to buzz. Warning: electronic ballasts are basically switching power supplies and are maybe hazardous to service (both in terms of your safety and